Turned on heat for the 1st time in 4 months boiler did not start

Luckycharm

Registered User
Messages
540
Not turned on the heat for 4 months at least and when I turned it on tonight. The boiler did not start there is a flashing light but does not seem to be working. Anyone know what I can do to try and get the boiler working again?
 
I turned mine off for a couple of months last year during the Summer and when I turned it back on it would not come on. I got someone out to take a look and it was just a blown fuse in the boiler !
 
Is it a gas boiler? Have you looked at the water pressure? It may be too low having not been on.
 
Yes it is a gas boiler - an Ideal model S24 mini boiler. The power green light is flashing and nothing else is happening - normally when I turn on the heat you can hear the boiler going on but nothing is happening- water pressure is low as well.
 
I know with mine when the pressure is low it wont start and i have to go up to the hotpress and turn a lever to until it gets up to 1.5 bar. Then turn the boiler pilot light back on.
 
Is there a smell of gas?

Perhaps the pilot light has gone out?

Get a certified plumber in to give it a service.

I assume the "rtfm" in post #3 means "read the full manual".

ONQ.

All advice on AAM is remote from the situation and cannot be relied upon as a defence or support - in and of itself - should legal action be taken.
Competent legal and building professionals should be asked to advise in Real Life with rights to inspect and issue reports on the matters at hand.
 
I assume the "rtfm" in post #3 means "read the full manual".

yeah, "full" that's right, sure :p ... As a Mechanical Engineer working with complex machinery and equipment, this is always my first response.
 
With low water on that boiler the pump should run, as it has only a water flow switch not a water pressure switch, so you should hear a hum

Is the green light 'on' or 'flashing'

Top up the water to 1 bar either way, make sure all your stats are turned up,
after a full summer off, at a guess, the pump is either stuck or a mv in the hotpress is stuck closed (money on the pump)

Everyone should turn their boiler on (gas and oil) every week or so, fo just a few minutes to avoid part seizing up (like pumps) as these tend to be all the callouts for this time of year (mostly pumps)

Always a good idea to schedule your yearly service to this time of year or even better late August where you may still get some summer discounts for servicing
 
With low water on that boiler the pump should run, as it has only a water flow switch not a water pressure switch, so you should hear a hum

Is the green light 'on' or 'flashing'

Top up the water to 1 bar either way, make sure all your stats are turned up,
after a full summer off, at a guess, the pump is either stuck or a mv in the hotpress is stuck closed (money on the pump)

Everyone should turn their boiler on (gas and oil) every week or so, fo just a few minutes to avoid part seizing up (like pumps) as these tend to be all the callouts for this time of year (mostly pumps)

Always a good idea to schedule your yearly service to this time of year or even better late August where you may still get some summer discounts for servicing


Green light is flashing- there is no noise whatsoever coming from the boiler.
 
try checking the thermostat - it could be set to a higher temperature than the current room temperature.
 
Ok, so when flashing the following applies....

a short pulse every 4 secs, boiler in stand by (no call for heat from external controls)
1 sec on, one sec off, boiler is in demand and trying to fire
fast pulse (4 per sec) boiler in fault mode

which do you have?
 
There is a common enough problem with the S24 which only occurs in Ireland (according to Ideal(UK) and their agent here). The pressure switch goes faulty (hydraulic end, not the microswitch itself) and they can't explain why. My own guess is that you have, what I have seen described here before as, a "semi-sealed system" i.e. it's a sealed system but incorrectly fed from the domestic storage tank in the attic. The Boiler never runs at its design pressure (above 1 bar cold) and down the road this causes a problems.

If you've managed to get the system pressure above 1 bar, checked and proved the motorised valve, as DGOBS said and, the boiler still won't start get a Registered Gas installer in.
 