Balcony/plug-in solar

From what I've investigated, the balcony hung solar panels have their own inverter (to convert the DC to AC) and feed the AC into the grid/house via a standard 3 pin socket. The inverter detects if there is no power coming into the house, and shuts down. This is the same process as Leo describes above. It will only provide power if there is power into the house.

So they operate exactly the same as the installed setup, but on a much smaller scale.
 
From what I've investigated, the balcony hung solar panels have their own inverter (to convert the DC to AC) and feed the AC into the grid/house via a standard 3 pin socket. The inverter detects if there is no power coming into the house, and shuts down. This is the same process as Leo describes above. It will only provide power if there is power into the house.
^^ Thats my understanding as well, just had my solar completed last Sat... would be interested in getting a few plug in ones aswell when they are allowed.. Some space left that would not be in SEAI grant guidelines, that plug in ones would be perfect for :)
 
You can't have someone working on the lines thinking the power is turned off and a surge of power flowing into what was thought to be an isolated ESB line from an unregulated source,
I hear this excuse all the time, but its never made sense to me. They don't switch off the power station on the other end of the line. We've all seen ads at some point in our lives telling us not to approach downed cables incase they are live. Do ESB workers just assume all cables are dead and hope for the best???
 
@AJAM there are isolators they can flip all over the place so the whole power station does not need to be powered off, but they are aiming to get the lines 'dead' so they can work on them safely. But if you imagine a break in the last 100m of wire approaching your house, they can isolate power coming from the grid towards the break but there is likely no isolator on the bit going to your house. So it's a cloudy day and they test the piece of wire coming from your house and a few neighbours; no power so they're good to go, then the clouds clear and there are hundreds of amps on that wire. In practice I'm sure they apply earths to both pieces of the broken wire, but the point is they are not expecting to be working on live wires and extra power sources add a lot of unpredictability.

What I wish they would do is work with the SEAI so it is clear to installers how they should go about wiring a system that allows for off-grid operation when the mains power is off that still qualifies for the grant. It's extremely common to have generator hookups in places like the US that work like this, so it's a solved problem technically.
 
It's extremely common to have generator hookups in places like the US that work like this, so it's a solved problem technically.
I had assumed it was fairly common knowledge how to configure the isolator/ transfer switch but a combination of consumers being unaware and providers not including them or pricier hybrid inverters by default to keep the quotes lower.
 
Seems my knowledge may be out-of-date actually @Leo. Back when I last looked at it (2021/2022 maybe) the wording from the SEAI appeared to specifically prohibit a transfer setup if you were using the grant, or that was certainly how most installers seemed to interpret it -

....Part B of the building regulations and I.S.10101, all domestic PV installations installed under this Scheme must:

• Provide an automatic (i.e., automatically operated by disconnection of the main AC supply to the building) shunt (or interlocked) isolation of the circuit (whether AC or DC, and two pole) from the solar PV modules into the building, as close to the solar PV modules as possible, and a maximum of 1.5m internally from the point of cable entry to the building. • Where the circuit from the solar PV modules does not enter the building, this point of automatic isolation must be within 1.5m of the solar PV modules. • For ground mounted system the shunt (automatic isolator) must be within 1.5m of the solar PV modules.

• This system of isolation shall automatically isolate the circuit from solar PV modules when the AC supply is disconnected to the building, i.e., a shunt or interlocked isolation function.

• ‘Shunt’ or ‘interlocked’ isolation of the DC circuit is the only acceptable manner of meeting the Building Regulation TGD B – Fire Safety (2017) for the purposes of this Scheme.

• For the avoidance of doubt the disconnection of the circuit from the solar PV modules must be automatic and operated by removal of AC supply to the building and must not be operated by means of a dedicated switch, pushbutton, ‘fireman’s switch’ or other manner.

• For the avoidance of doubt an isolation of the supply from the PV modules is required in ALL cases, whether micro-inverters, DC optimised inverters, where the inverter is within 1.5m of cable entry or any other configuration is used.



Now SEAI have a page dedicated to powering your home from solar/battery during a power outage which is great - https://www.seai.ie/blog/solar-panels-power-cut
 
Ok I looked into this, the problem in the UK and Ireland is use of BS 1363 ring loop circuits and older AC type RCDs (residual current device). They detect AC current rather than the DC current solar produces and so might be unaware of the additional load created by solar power, which in turn could overheat copper cabling. Makes sense now. Germany typically use radial circuits rather than the British style loops
 
Ok I looked into this, the problem in the UK and Ireland is use of BS 1363 ring loop circuits and older AC type RCDs (residual current device). They detect AC current rather than the DC current solar produces and so might be unaware of the additional load created by solar power, which in turn could overheat copper cabling. Makes sense now. Germany typically use radial circuits rather than the British style loops
Looks like a lot of these concerns may have been put to bed. I'm no expert but check this out ...
 
Barry Heneghan TD has been quite vocal on the subject of plug in solar / solar for apartments, and comes with some relevant educational qualifications, if you look up his profile.

The fact that he's one of the independent TDs working with Government might even see him have some influence.... well, we can live in hope, I suppose !
 