adding thermostate to circulating pump

brian

Registered User
Messages
45
Hi,

I have a circulating pump that is attached to a back boilder in my fireplace.
I would like to add a thermostat so I do not manually have to turn on/off the pump i.e it senses when the water is getting warm when I light the fire and automatically switches on/off the pump.
Its a standard grundfos domestic pump.

What is the easiest/cheapest way to do this?

thanks in advance,

Brian
 
Buy a pipe thermostat from any plumbing suppliers, check with continuity meter and wire to circulating pump. Make sure you fit the pipe stat on the flow pipe from the back boiler as close to the back boiler as possible.
 
Hi,

thanks for replying Shane.
I will look into the option of getting a pipe thermostat,

Brian
 
Pipe stat is the way to go, just break the cable supplying pump and run it thorough stat. Stat should cost no more then €15.
 