Thanks onq
The vent is approx 1m from the top of the door leading on to the balcony and 1.5m from a permanent ventilation grille.
I've uploaded a photo of it here to help show what I'm on about!
[broken link removed]
Bejaypers!
Is that a covered balcony?
Is there one above yours or a roof?
And is that a return wall to the left there, effectively enclosing it on that side?
Unless you have odd sized bricks or coursing, each course [brick + mortar joint] is 75mm high.
The bottom of the vent seems to be only 8 courses of bricks above the door ope.
Thats 8 x 75 = 600mm, or well below the height required.
The vent seems to be about two bricks away horizontally [225 x 2 = 450mm] i.e. well withing the 3.0M distance.
Its difficult to be certain without measuring it on site, but this vent installation may be non-compliant in terms of distance.
In addition, the siting of such a vent in a building return and under an overhang seems to raise issues not dealt with in the example given by the Technical Guidance Document.
The following questions arise; -
- Why didn't the builder use a ventilated stack system dropped vertically through the building for each apartment and fire-proofed at each floor level?
- Given the likely problems with the location of the vent, why didn't he route them to high level away from all the balconies?
This opens up a whole other can of worms, e.g. given the repeatibility of apartment modules in a block, you may not be the only one suffering the effects you describe.
Other questions may arise:
- were Opinions of Compliance offered by an architect?
- Did the builder and/or the plumber offer certificates?
- is there a management company?
- is the builder still around?
- is he solvent?
Either way, it looks like they may have a case to answer.
If you need further advice, let me know.
We do this kind of thing for a living.
ONQ.