plumbing boiler stoves to you

Status
Not open for further replies.

foxy 6

Registered User
Messages
1
I have dual system solid fuel and oil. My problem is if de stove is on for a while de pipes start banging. It's on zoneed system I manually opened z2 it stopped it any advice
 
the water in the solid fuel boiler is reaching over temp and the pump is possible not pumping, by opening both zones your releasing the hot water to a greater area and reducing the temp,
would be best to have just one boiler on at any time its not ideal to have both working together

check the pump for the solid fuel and see what temp its set at, its possible its set to high usually 55 deg is about right
 