Hi, could you elaborate? Is it each circuit or each switched point?
If it's each domestic circuit, then the maximum permisseable load is 10amps, as per breaker rating on board.
If it's each switched point then the actual load would be the addition of all the wattages of bulbs divided by operating voltage (230v).
(*Note. Fluorescents and other inductive circuits have a higher switching load)
Thanks SineWave, I'm talking about switched points. I want to put in three 50W recessed lights in a room. Just want to be sure I'm not overloading the circuit.