Hi Stevo32, I would stick with the manufactures agent but see if there is another one you can get a second opinion from, i would stay away from Bord Gais as they can be very hit and miss with a funky fault. At this stage the engineer should have been able to rule out a boiler component, he would do this by replacing them, he may not know what's causing it but he should know what isn't, the flow switch and body should be replaced as a minimum, this is due to the design which can make them erratic and the fact that it's susceptible to sludge, if it had been replaced a good engineer could determine if sludge is a problem( Davy unfortunately i find contamination can occur after as little as 3 months especially if inhibitor has been added to a unflushed system) , the PCB would be second on my list to prove it's OK, i wouldn't think it's the PCB because it would be more erratic and your fault seems to be heat orientated, i would try turning down your boiler stat and manual opening your heating zone valve as a test to see if it has any impact on your fault, sometimes when the circuits close down and the boiler is still running the boiler can detect this as a flow problem because of the larger restriction and shut down, air in the system could be another factor if you did have a lump of air running around it could effect the flow switch but again it would be more erratic, so long story short it's wat Davy and DGOBS said, Gary